triptolemus
Member
- Location
- California
- Occupation
- Safety
I have a difference of opinion on an interpretation I am looking to settle. 590.4(J) states, among other things, that cable assemblies and flexible cords and cables installed as branch circuits or feeders shall not be installed on the floor or on the ground. Then it states that extension cords are not required to comply with 590.4(J).
What has been happening here is that the AHJ has required that generator cables be installed on top of a plywood "tray" when they are ran on the ground or floor to meet the requirements of 590.4(J). It has been suggested that a Type W 4/0 cable with PowerLock connectors at both ends is an "extension cord" and exempt from 590.4(J). The counter to this is two-fold; that the cords are feeders and generator cables are not what would commonly be known as an "extension cord". Naturally, one problem is that "extension cord" isn't defined. One definition I did find: Extension cords, also referred to as portable cords, are used for temporary power connections requiring a flexible cord seems to fit the generator cables.
Is 590.4(J) just poorly written?
What do you think?
What has been happening here is that the AHJ has required that generator cables be installed on top of a plywood "tray" when they are ran on the ground or floor to meet the requirements of 590.4(J). It has been suggested that a Type W 4/0 cable with PowerLock connectors at both ends is an "extension cord" and exempt from 590.4(J). The counter to this is two-fold; that the cords are feeders and generator cables are not what would commonly be known as an "extension cord". Naturally, one problem is that "extension cord" isn't defined. One definition I did find: Extension cords, also referred to as portable cords, are used for temporary power connections requiring a flexible cord seems to fit the generator cables.
Is 590.4(J) just poorly written?
What do you think?