5kv to 480v xfrmr

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
5kv switch is feeding xfrmr which is feeding the 800a panel. Anyway to determine size of 5kv switch or xfmr based only 480v switch size of 800a given? Thanks
c4ccf7a1145fbfae329c35a92936b809.jpg


Sent from my SM-N960U using Tapatalk
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
All you can get is a rough guess if you assume the maximum load is actually 800A. That equates to roughly 650kVA at 480V, which will be around 95A at 4160V on the primary (5kV is the “class” of equipment, the actual utilization voltage will be 4160V in North America). The smallest typical 5kV switch will be 200A anyway.
 

topgone

Senior Member
If the OCPD is 800A, it would mean a full load of 800*.80 = 640A. The nearest standard transformer at 480V should be 500kVA (FL=674A). At 4160V, the full load amps will be 78A. A 150E fuse could protect the primary of the transformer.
 

mstrlucky74

Senior Member
Location
NJ
Thank you. I got that @ 800A 480v side( even 640A) I would need a 500kva xfrmr. So I could fuse the 5kv switch at 150A and then I'd need to run 150A feeder from 5kv switch to primary of 500KVA xfrmr?
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
Can you get them from the same manufacturer and buss them together? 5k,xfmr,mdp. or isn't there room?
 

mstrlucky74

Senior Member
Location
NJ
Can you get them from the same manufacturer and buss them together? 5k,xfmr,mdp. or isn't there room?

I def have the room. So sort of like a substation line-up but usually that's only the 5kv step don xfrmr and the 480v distribution. I could get the 5kv switch/xfmr and MDP as one? Thanks
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
That I don't know as a one piece.
You can get the three so they just bolt together like one piece.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
If the OCPD is 800A, it would mean a full load of 800*.80 = 640A. The nearest standard transformer at 480V should be 500kVA (FL=674A). At 4160V, the full load amps will be 78A. A 150E fuse could protect the primary of the transformer.

I would not assume the .8 loading is going to be appropriate. Typically 480V equipment at this rating, i.e. 800A is going to be 100% rated. For sizing I would not make that assumption anyway.
 

mstrlucky74

Senior Member
Location
NJ
So if I have a 5kv switch feeding a 500kva transformer(5kv to 480v) which then feeds 800A 480v distribution panel. If the 5kv switch is fused at 150A would it just be 150A conductors to the prim. Side of the 5kv xfrmr? And the secondary side of the xfrmr I would need conductors for 800A? Thanks.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So if I have a 5kv switch feeding a 500kva transformer(5kv to 480v) which then feeds 800A 480v distribution panel. If the 5kv switch is fused at 150A would it just be 150A conductors to the prim. Side of the 5kv xfrmr? And the secondary side of the xfrmr I would need conductors for 800A? Thanks.

Yes. What manufacturer are you using? Eaton makes switch and transformers that mount together. This is a step-up but you can get the idea: