5KVA Transformer 480-208/120V breaker sizing
Cartoon1
Florida
Electrical Engineer
Hello. I have a long distance run to a equipment (exterior) that needs a 240V for input single phase. I'm running a 480V from the panel to a small 6KVA stepdown transformer near the equipment. This equipment draws 15Amps single phase at 240V. My understanding is the closest transformer to handle the load is a 5KVA transformer. I'm placing the transformer near the equipment after the long 480V run about (300Feet).
Per Table 450.3(B):
Primary: 5KVA / 480V = 13A * 1.25 = 13.02A. The closest breaker is a 15A breaker at the 480V panel.
Secondary: 5KVA / 240V = 20.8A * 1.25 = 26.04A. I'm putting secondary disconnect switch rated (30A) with 25A fuse.
Is my calculations okay? would it be better/permissible to change the breaker to 20A for primary? And do small transformers come with an integrated overload device?
Thank you,
Per table 450.3 the primary is allowed to be 250% so 13A * 2.5 = 32.5A. Since I don't see the "next larger breaker size" for this I would say you need to use a 30A maximum breaker on the primary.
You mentioned 6 kva.... That is normally a 3 phase transformer
Are we looking at 3 phase or single phase ??
I suggest you use a Sq D Mini Power Zone. It’s an all in one primary disconnect, 5 Kva transformer and secondary panel, it’s NEMA 3R rated. Set a post, drive 2 ground rods and you are done. I have used at golf courses and for scoreboards. Other manufactures may have a similar product.
I need to look into that, it will make my life easier. Does it come with a primary and secondary breaker? Or just a disconnect switch?
Thank you,