5kva transformer
UL-508 does require a grounding electrode terminal stats the following:
16 Transformer and Power Supply Secondary Grounding
16.1 A secondary circuit that contains field wiring terminals and is supplied from a power transformer, control transformer, or power supply shall have the secondary grounded under any of the following conditions:
a) When the secondary voltage is less than 50 volts; and
1) The supply to the primary is over 150 volts to ground; or
2) The supply to the primary at any voltage is ungrounded;
b) When the secondary voltage is 50 volts or greater and the secondary circuit is able to be
grounded so that the maximum voltage to ground on the ungrounded conductors does not
exceed 150 volts;
c) When the secondary is a 3-phase, 4-wire, wye connected in which the center point of the
wye is used as a circuit conductor; or
d) When the secondary is a 3-phase, 4-wire, delta connected in which the midpoint of one
phase winding is used as a circuit conductor.
Revised 16.1 effective March 1, 2007
16.2 A transformer or power supply secondary that is required to be grounded in accordance with 16.1, shall have a main bonding jumper factory connected to the secondary and to the enclosure and grounding electrode conductor terminal (or only to the enclosure when a grounding electrode conductor terminal is not provided). The size of the main bonding jumper shall be as specified in 75.1.4, based on the secondary rating. A grounding electrode conductor terminal sized to retain the required grounding electrode conductor in accordance with 75.1.4, based on the secondary rating, shall be provided in the enclosure containing the transformer or power supply and a marking as specified in 54.10 shall be provided.
Exception: When the transformer is rated not more than 1000 volt-amperes and supplies only control circuits, the grounding electrode conductor terminal is able to be omitted and the main bonding jumper shall not be smaller than a No. 14 AWG (2.1 mm2) copper conductor. The jumper is not otherwise required to be larger than the phase conductors connected to the transformer secondary.
Revised 16.2 effective March 1, 2007
16.3 When components marked with a slash voltage rating, such as 120/240V, 480Y/277V, or
600Y/347V, are provided on the secondary side of a power transformer or power supply, the secondary shall be grounded as in 16.1(b), 16.1(c), or at the center point of the wye for a 3 phase, 3 wire secondary circuit, and 16.2.
Added 16.3 effective March 1, 2007
So now if you have a 4 story concrete building with a 480 volt feeder to a power panel located in a equipment room in penthouse on the roof and the only transformer a 5kva 480v to 120v control voltage transformer for a control panel, would apply 250.30(A)(3) exception (3)? It seem to me it would be more effective to have every thing bonded to the secondary side of the control voltage transformer.