Hi all,
Customer removed an old hot tub and wants to convert the existing feed (6/2 Romex) for the old 60A 240V hot tub circuit into a sub panel to service additional branch circuits in the basement living space (I'd normally insist on running new feed, but its clear on the other side of the building, 100' from the main panel, all finished spaces, and would be a nightmare to run).
I think we're good, but I just figured I'd check here to see if there's anything for the inspector to nitpick. Subby's plan is this:
At the main, remove the old 60A 2-pole breaker, install new 60A single-pole breaker (and another breaker to fill the space), swing neutral of 6/2 feed to neutral/ground bus.
At the sub, bond hot conductor from feed to one of the two hot busses, jumper one hot bus to the second. Bond neutral to neutral bus. Install separate ground bus, bond ground from 8/2 feed to ground bus.
Load will be two 20A circuits and one 15A, for a total of 55A of load.
So what is inspector going to yell at us for?
Customer removed an old hot tub and wants to convert the existing feed (6/2 Romex) for the old 60A 240V hot tub circuit into a sub panel to service additional branch circuits in the basement living space (I'd normally insist on running new feed, but its clear on the other side of the building, 100' from the main panel, all finished spaces, and would be a nightmare to run).
I think we're good, but I just figured I'd check here to see if there's anything for the inspector to nitpick. Subby's plan is this:
At the main, remove the old 60A 2-pole breaker, install new 60A single-pole breaker (and another breaker to fill the space), swing neutral of 6/2 feed to neutral/ground bus.
At the sub, bond hot conductor from feed to one of the two hot busses, jumper one hot bus to the second. Bond neutral to neutral bus. Install separate ground bus, bond ground from 8/2 feed to ground bus.
Load will be two 20A circuits and one 15A, for a total of 55A of load.
So what is inspector going to yell at us for?