Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
Every HVAC person always tells me to run a 6-2 on a 60 amp breaker for a furnace or heat pump. But #6 romex is only rated for 55 amps, correct ?
Yes and a wildly common violation.Every HVAC person always tells me to run a 6-2 on a 60 amp breaker for a furnace or heat pump. But #6 romex is only rated for 55 amps, correct ?
10kw heat strip is only 41.6 ampsEvery HVAC person always tells me to run a 6-2 on a 60 amp breaker for a furnace or heat pump. But #6 romex is only rated for 55 amps, correct ?
I agree if you just are powering the heat strip. As I recall most AHs for 10 KW will need a blower that will put it over 55 amps. The only sure way is to look at the MCA and Max OCPD for the equipment involved.10kw heat strip is only 41.6 amps
Multiply by 1.25 and you're at 52.08 amps
Wire good for 3 amps more
Nobody makes a 55 amp breaker, so you move up to 60
Good solution but stupid code rule. Why would SE cable be any better than NM cable for this load?Most of the HVAC guys here have switched to using #6 SE cable with an ampacity of 65 amps
Good solution but stupid code rule. Why would SE cable be any better than NM cable for this load?
Don't forget about ambient temperature adjustment, which allows an 8% ampacity increase for NM if temp is between 69⁰ and 77⁰ Fahrenheit
That makes 6-2 good for 59 amps in almost any indoor furnace setting exceptView attachment 2561706
I'm not following how you come to that.Perhaps if it was not NM cable, 334.80 limits the ampacity of NM to the 60C column, so the way I read it no up-rating allowed.
334.80 second sentence statesI'm not following how you come to that.
So the way I was taught you can't ever uprate nm cable to an ampacity above that in the 60C column.The allowable ampacity shall not exceed that of a 60°C (140°F) rated conductor.
The 90°C (194°F) rating shall be permitted to be used for ampacity
adjustment and correction calculations, provided the final calculated
ampacity does not exceed that of a 60°C (140°F) rated conductor.
The ampacity in the chart is only applicable under a specified ambuet temperature condition - 30⁰C or 86⁰F334.80 second sentence states
So the way I was taught you can't ever uprate nm cable to an ampacity above that in the 60C column.
I guess that is perfectly reasonable for a furnace, if the thermostat can be configured to lock out temperatures above 77F, and the wiring is within the same ambient.Don't forget about ambient temperature adjustment, which allows an 8% ampacity increase for NM if temp is between 69⁰ and 77⁰ Fahrenheit
Cant argue with that, I stand corrected.If your ambient temperature changes, so does the ampacity of the wire