Hello all,
A 3hp 230 volt dust collector came equipped with a 6-20P cord cap from the factory. Table 430-248 has the FLC at 17 amps, creating a red flag for me. However when the unit is plugged into a 6-20R receptacle on a 2 pole 20 it trips within 10 seconds from the inrush current (approx 55 amps on the meter). When diagnosing the problem a 30 amp breaker was installed to check the current. The 30 amp breaker held during inrush and leveled off at 14-15 amps. Is it permissible to install a larger size breaker per Table 430.52 (up to 250%) on an individual branch circuit feeding a single 6-20 receptacle? I would rather not cut the cord and hardwire potentially voiding the listing of the equipment.
Thanks
A 3hp 230 volt dust collector came equipped with a 6-20P cord cap from the factory. Table 430-248 has the FLC at 17 amps, creating a red flag for me. However when the unit is plugged into a 6-20R receptacle on a 2 pole 20 it trips within 10 seconds from the inrush current (approx 55 amps on the meter). When diagnosing the problem a 30 amp breaker was installed to check the current. The 30 amp breaker held during inrush and leveled off at 14-15 amps. Is it permissible to install a larger size breaker per Table 430.52 (up to 250%) on an individual branch circuit feeding a single 6-20 receptacle? I would rather not cut the cord and hardwire potentially voiding the listing of the equipment.