6.9KV Conduit Spacing in Ductbank

Status
Not open for further replies.

smkdeb123

Member
Location
Charlotte, NC
I have a 8 X 3 concrete ductbank, 8 columns, 3 rows, all 4"PVC. Top roll is 6.9KV 3/c-500kcmil, middle roll is all future, bottom roll is 480v MOV power, control, etc. The question is on Figure B 310.3 the voltage only is listed for 0 to 5000 volts, where in the code does it address the separation of conduits based on higher voltages? How about 13.8KV? The top of the duct bank is 30" below grade.
 
The analogous figure for higher voltages is Figure 310.60. The problem is the various table values (Table 310.67 through Table 310.86) are very specific to Figure 310.60, including spacing.
A few adjustments are recognized in Section 310.60 and Section 310.60 FNP refers you to Annex B. The basic applied formulas are the same; it is the ?constants? that vary.
 