Can you install 6 circuits (9 wires) of #12 thhn in one conduit under the following conditions:
Given:
? 20 amp single pole breakers (not concerned with handle tie code issue for now)
? 6 circuits in one conduit ? phase A,B,C, and N, Phase A,B,C and N, 1 equipment ground)
? Assume a continuous load of 16 amps or less per circuit of T8 -32 watt fluorescent lights with electronic ballasts
? Assume voltage at panel is 120/208 3 phase 4 wire
? Assume ambient temperature is 110 degrees F
Not sure if the below is correct:
? Do you derate for 4-6 conductors @ 80% or
? for 7-9 conductors @ 70% because the fluorescent lighting makes it a non-linear load with harmonics where the 2 neutrals are carrying more than the unbalance?
Step 1--------#12 thhn. 90 degree column = 30 amps x .87 for ambient temperture = 26.1 amp
Step 2--------26.1 amp x 80% (4-6 conductors ? neutral only carrying imbalance) = 20.88 amps or
or
26.1 amp x 70% (7-9 conductors ? neutral carrying more than unbalance because nonlinear/harmonics
present) = 18.27 amps
1. Is the ampacity of the #12 now 18.27 amps?
2. Does the installation still meet NEC code because?.
A continuous load on a 20 amp breaker can be no more than 80% or 16 amps??and the newly derated #12 wire now has an ampacity of 18.27, which is greater than the 16 amp load?
Given:
? 20 amp single pole breakers (not concerned with handle tie code issue for now)
? 6 circuits in one conduit ? phase A,B,C, and N, Phase A,B,C and N, 1 equipment ground)
? Assume a continuous load of 16 amps or less per circuit of T8 -32 watt fluorescent lights with electronic ballasts
? Assume voltage at panel is 120/208 3 phase 4 wire
? Assume ambient temperature is 110 degrees F
Not sure if the below is correct:
? Do you derate for 4-6 conductors @ 80% or
? for 7-9 conductors @ 70% because the fluorescent lighting makes it a non-linear load with harmonics where the 2 neutrals are carrying more than the unbalance?
Step 1--------#12 thhn. 90 degree column = 30 amps x .87 for ambient temperture = 26.1 amp
Step 2--------26.1 amp x 80% (4-6 conductors ? neutral only carrying imbalance) = 20.88 amps or
or
26.1 amp x 70% (7-9 conductors ? neutral carrying more than unbalance because nonlinear/harmonics
present) = 18.27 amps
1. Is the ampacity of the #12 now 18.27 amps?
2. Does the installation still meet NEC code because?.
A continuous load on a 20 amp breaker can be no more than 80% or 16 amps??and the newly derated #12 wire now has an ampacity of 18.27, which is greater than the 16 amp load?