I came into a came situation, where there is a #6 wire on a 90 amp breaker, the line side feeds a disconnect fused at 50 amps, on the load side it feeds an air compressor,
per the manufacture specs and name plate + 125%, it is fused correctly. the Question is, I can not find any thing In the NEC, that would say it is OK, to put a #6 THHN copper wire on a 90 amp breaker 75 deg, and I ask the person that did, and was told It is OK, nothing will happen.
Well, what I understand, on the load side side a ground fault and/or short will open the OCPD, but, the line side, the wire would melt and/or burn, and pose a probable elect
Thank you, for any information, and concerns.