Kalos
Member
- Location
- Clermont, FL
I have a project in an existing shopping center with an underground service lateral feeding a trough that supplies (5) meter disconnects. (no main disconnect is present) (1) of the occupancy services has a CT meter and Ct box mounted under the trough with no disconnect present. (the disconnect is located in the interior of the tenat space) We need to install (2) new 200 amp services for (2) new tenant spaces which brings the total number of disconnects (7).
I brought up the (2) obvious points with the engineer- 1) The disconnects are not grouped and 2) there are more than (6) disconnects.
The engineer believes that 230.2 & 230.40 exception #1 makes this OK. I admit this is a bit unclear to me. Can someone help explain why this is alright?
I brought up the (2) obvious points with the engineer- 1) The disconnects are not grouped and 2) there are more than (6) disconnects.
The engineer believes that 230.2 & 230.40 exception #1 makes this OK. I admit this is a bit unclear to me. Can someone help explain why this is alright?