Hello, I have looked over the forums and though the six disconnect rule is discussed the following question has not been addressed that I am aware of. I am aware of the codes surrounding when and how to apply the 6 disconnect rule; my question is "What are the benefits to going with a single main disconnect?" The scenario I am running into is regarding an industrial application. We are replacing an old 5kV service with a new 480/277V secondary service. The new main switchboard is to be a 1600A board. The original design showed a 1600 Amp main in the incoming section and (3) feeder circuit breakers in the distribution section. The cost that came back on this gear higher than the client was anticipating. (Poor expectation management by others) So in order to drop the cost I sent out an alternate design showing the removal of the main circuit breaker while utilizing the 6 disconnect rule. The main switchboard price was cut in half and was able to be reduced to 1 section. I have a discussion coming up with the owner to explain the pro's and cons of this decision. The cons I have came up with for the 6 disconnect rule are 1. It reduces flexibility for future expansion later down the road by limiting the amount of feeders that can be derived from that board. 2. there is a minor safety concern when shutting down the building due to the multiple switches (Unqualified guy hits 1 of the 3 switches thinking the building is down before servicing...zap) Beyond that I cannot come up with anything. Does it impact how a fault is cleared? What justifies the additional cost of the gear to go with a single main disconnect if it is justifiable at all?