My customer has a 3 story medical building with meters in the basement 120/208 single phase. We have a 2nd floor conference room that needs to be metered by itself. There's a 100-amp breaker in the empty meter space, but I'd prefer to set a 60-amp panel in the suite because the load is minimal. It's about 165' run. I'd really rather run 1" conduit with #6 vs 1-1/4 with #3.
A cursory search of the internet doesn't show a 60-amp breaker available. Square D QE breaker. I haven't explored the unconventional limits of what the code might allow (normal circumstances, you just plug in a 60-amp breaker) but can I tap #6 (or 4 if i decide to for VD) and protect for short circuit using the 100-amp breaker and protect for overcurrent at the panel in the suite with a 60-amp main breaker?
A cursory search of the internet doesn't show a 60-amp breaker available. Square D QE breaker. I haven't explored the unconventional limits of what the code might allow (normal circumstances, you just plug in a 60-amp breaker) but can I tap #6 (or 4 if i decide to for VD) and protect for short circuit using the 100-amp breaker and protect for overcurrent at the panel in the suite with a 60-amp main breaker?