#6 Feeder 100-amp breaker at meter, 60-amp breaker at panel
Jps1006
Northern IL
My customer has a 3 story medical building with meters in the basement 120/208 single phase. We have a 2nd floor conference room that needs to be metered by itself. There's a 100-amp breaker in the empty meter space, but I'd prefer to set a 60-amp panel in the suite because the load is minimal. It's about 165' run. I'd really rather run 1" conduit with #6 vs 1-1/4 with #3.
A cursory search of the internet doesn't show a 60-amp breaker available. Square D QE breaker. I haven't explored the unconventional limits of what the code might allow (normal circumstances, you just plug in a 60-amp breaker) but can I tap #6 (or 4 if i decide to for VD) and protect for short circuit using the 100-amp breaker and protect for overcurrent at the panel in the suite with a 60-amp main breaker?
You can easily pull 3-#3 & 1-#8 through 1" EMT/PVC/Rigid to stay with 100 amps.
If you really want to run 60 amps is there a place in the meter room you can set a single circuit breaker enclosure? if so run 100 amp conductors to that and install a 60 amp breaker for the feeder to the conference room. It will cost more to do this then just staying with 100 amps.
Stay conventional and put in the correct breaker for whatever size wire you're pulling.
JAP>
You need to protect the new conductors supplying your new 60A panel by installing a properly rated OCPD at the source end.
Thanks guys. I was hoping someone would point out a way to apply a tap rule that would apply, since I couldn't find one myself. Material cost is around $1000 or so more to use the larger cable, I'm going to go that route. My supplier says they didn't make a 60-amp QE breaker so I'm stuck with the spare 100-amp on site (I'm glad there was one). I may consider Curt's suggesting to pull #3's through 1".
Thanks again!
If the load is minimal and you want to reduce the feeder size to the subpanel and a 2p 60 is not available maybe they make a 2p 50,40,30 etc... and you could drop the conductor size down as needed.
JAP>
I don't really know anything about Square D's product lineup outside of residential (@jim dungar does), but QE270VH is apparently an available (refurbished?) product, if that would be the 70A breaker required, and if you prefer 70A to 100A.
Cheers, Wayne