If you install an EGC you can make them as long as you like but, you might need to use a different term than fixture "whip" for real long ones. :smile:
Supporting them is the issue once you get past 6' it changes how many times it needs supporting. I would hope you put a grounding conductor in them even if less then 6' :smile: I've seen to many pulled apart at the fittings.
Typical 3/8" FMC whips are only permitted in lengths up to 6' regardless of whether or not they contain an EGC. Longer than 6' and you'll need to use 1/2" or larger FMC. Look at 348.20(A)(2).