NEC 2020I am doing a hot tub install for a friend. I have not done one for quite a while. I was told that the 6 ft rule on non metallic flex is no longer in affect. Is that true? I have misplaced my code book on a job site,
otherwise I could look up myself.
That is not new and the permission to use LFNC in lengths longer than 6' goes back the the 99 code when LMFC was still in the same article as LFMC.NEC 2020
This is new.
Article 356.10 (5)
Type LFNC shall be permitted to be installed in lengths longer than 1.8 m (6 Ft) where secured in accordance with356.30
or 12 inches from fittings and every 3 feet there after
Ok, my bad, I seen it highlighted and I was at work so I assumed it was new.That is not new and the permission to use LFNC in lengths longer than 6' goes back the the 99 code when LMFC was still in the same article as LFMC.