Looked in a ditch the other day where (3) sets of 200 amp service conductors were coming from a padmount transformer to (3) individual 200 amp meter mains mounted on a rack.
(3) Groundrods were driven in the ditch roughly 6" apart about 10 feet from the meter location ,then, another 3 were driven 6" apart roughly 20' from the meter location for a total of (6) rods.
They took a #6 bare from each meter and caught (2) rods each. One at 10' away and one at 20' away as individual applications.
They did not bond any of the rods together.
To me this was an overkill but seeing as how they did install all the rods I feel they should have all been bonded together.
Couldn't the rule have been satisfied by taking the #6 GEC from each meter to (2) rods total ?
JAP.