Hello All,
Installing 36 Sunpower AC modules. Each Module is rated at 1.33 Amps AC, 36 x 1.33 x 1.25= 59.85 Amps AC.
We will be combining the module outputs into a combiner panel, which will itself have one output to feed the meter and main panel.
Seeing as #6/3 NM is only rated to 55 amps, am I right coming to the conclusion that it cannot be used here, even though i am pretty certain that wire will never see 55 amps on it, due to losses and the fact that we oversize it for continuous use?
Any thoughts on this?