This is the code question.
1. 210.8 (A) (1) through (10)
(7) Sinks - where receptacles are installed within (6 ft) of the outside edge of the sink. (GFCI is required)
1. I have a inspector telling me that the disposal under the sink which has a receptacle that is cord plugged into, needs to be GFCI protected. I disagree with him because it is under the sink and not along counter top. what is your thought on this?
2. The same inspector is also saying that the outlet under the sink cannot be a GFCI or a Arc fault receptacle because it is not readily accessible article 100 . Capable of being reached quickly for operations, renewal, or inspections without requiring those to whom ready access is requisite to actions such as to use tools, to climb over or remove obstacles, or to resort to portable ladders, and so forth. (He is saying that they could stack something in front of it so it will not be ready accessible.) What is your thoughts on this? ( to me they can stack something on a counter top or put a portable microwave in front of it than by his logic that would also not be allowed because it would than not be ready accessible)
This is an issue is because there are 100 units on this site that will have to have this outlet relocated, and there is asbestos in the dry wall mud that would have to be remediated. Any feed back you can provide is appreciated. Thank You