Aloha, Mike Holt Forum
In the NEC 08'- Article 210.52 (A) (1) Spacing states;
Receptacles shall be installed such that no point measured horizontally along the floor line in any wall space is more than 1.8m (6' ft) from a receptacle outlet.
The question...
Six feet from the door way is a receptacle then six more feet should be a receptacle.
In many illustrated diagrams shows - Six feet from the door way is a receptacle then twelve more feet would be a receptacle.
I do not understand where the magic number of twelve is in the stated article.
However from experience I know that six than twelve is correct.
Why is this? Does something to do with a six foot cord attached to a lamp? From what I understand from the Article six foot and twelve foot is not to code.:-?