Greetings all I was out to look at a enphase AC solar system about to be installed on new home, the electrician wiring the house (not affiliated) ran a 6/3 from the service to the enphase combiner panel (3-ES i believe)
And landed a 60A breaker at the bottom of all the installed breakers but not the bottom of the loadcenter.
This got me thinking the 60 amp feeder from AC combiner panel is a "power source output circuit" and the breaker needs to comply with 705.12(B)(3) right?
So for a 200A panel the max size breaker is 40 amps and the breaker needs to be moved the the opposite end of the bus from the main right?
The actual output from the microinverters is less than 5kw, well below 40 amps.
And landed a 60A breaker at the bottom of all the installed breakers but not the bottom of the loadcenter.
This got me thinking the 60 amp feeder from AC combiner panel is a "power source output circuit" and the breaker needs to comply with 705.12(B)(3) right?
So for a 200A panel the max size breaker is 40 amps and the breaker needs to be moved the the opposite end of the bus from the main right?
The actual output from the microinverters is less than 5kw, well below 40 amps.