Jps1006
Member
- Location
- Northern IL
I have a piece of equipment 250-volt 3-phase fed from an SOOW 8/4 drop cord with a waterproof pin and sleeve connector rated at 60-amp fed from a circuit on a 40-amp breaker.
Next to it is another machine with an identical setup, except it's fed from a 30-amp breaker.
Next to it is another machine with an identical setup except it's fed from SOOW 10/4 on a 20-amp breaker (all 60-amp pin and sleeve connectors).
Code violation?
(NEC 2011) 210.20 (b)(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
What am I missing?
Next to it is another machine with an identical setup, except it's fed from a 30-amp breaker.
Next to it is another machine with an identical setup except it's fed from SOOW 10/4 on a 20-amp breaker (all 60-amp pin and sleeve connectors).
Code violation?
(NEC 2011) 210.20 (b)(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
What am I missing?