Hello
I am having a inground pool installed and I am doing the sub panel installation. Can someone confirm my calculations are correct.
Thanks
60 amp breaker at main panel
3/4" emt conduit in house approx 10 ft
3/4" IMC conduit outside approx 4 ft
3 conductors at #6 copper wire
1 conductor for ground #8 wire
Outdoor rated 6 space 12 circuit 100 amp sub panel
No external grounding rod
separate terminal for ground conductors in sub panel
Thanks
I am having a inground pool installed and I am doing the sub panel installation. Can someone confirm my calculations are correct.
Thanks
60 amp breaker at main panel
3/4" emt conduit in house approx 10 ft
3/4" IMC conduit outside approx 4 ft
3 conductors at #6 copper wire
1 conductor for ground #8 wire
Outdoor rated 6 space 12 circuit 100 amp sub panel
No external grounding rod
separate terminal for ground conductors in sub panel
Thanks