What temperature column are we allowed to use in sizing the conductors for a 60 amp subpanel (for a pool powering application in this case)? Thanks in advance for your responses. e/m
 
Most all equipment is rated at 75 C. So you would use the 75 C column. Make sure conductors are rated at least at 75 C. 334.80 allows NM-B rated at a max of 60C but should not be using NM for a pool sub-panel because a insulated EGC is required.
 
mistermudd said:
Most all equipment is rated at 75 C. So you would use the 75 C column. Make sure conductors are rated at least at 75 C. 334.80 allows NM-B rated at a max of 60C but should not be using NM for a pool sub-panel because a insulated EGC is required.
Thanks Mr. Mudd, appreciate your response. e/m.
 