Carultch
- Massachusetts
Can't say any are compliant without an OCPD rating!
Assuming 60A OCPD, all could be compliant. #6 requires load to be less than 55A... but it being a potential smallest size conductor IMO in no way limits one from choosing a #4 as the smallest size, i.e. using 240.4(B) is optional; lack of using 240.4(B) cannot be used to penalize one on another requirement.
These are irrelevant when based on 60°C size as permitted in 110.14(C)(1)(a)(2).
I did intend there to be a 60A OCPD, fully utilized at 48A continuous so that 240.4(B) wouldn't apply.
I think I get it. Please correct me if I am wrong.
It is optional to take advantage of 240.4(B)
It is also optional to take advantage of 75C terminals/90C wiring as allowed for exceptions to the defaults in 110.14(C) where applicable.
The value of "the minimum size that has sufficient ampacity for the intended installation" as is used for the starting point of upsizing the EGC wire can be based on conductor size WITH OR WITHOUT the two aforementioned options that can reduce it.