D dema Senior Member Location Indiana Aug 13, 2005 #1 60 degree ampacity Where does it say that conductors must be sized based on the 60 degree C rating for breakers 100A and under?
60 degree ampacity Where does it say that conductors must be sized based on the 60 degree C rating for breakers 100A and under?
iwire Moderator Staff member Location Massachusetts Aug 13, 2005 #2 Re: 60 degree ampacity Re: 60 degree ampacity Originally posted by dema: Where does it say that conductors must be sized based on the 60 degree C rating for breakers 100A and under? Click to expand... 110.14(C)(1) But it also says "unless marked otherwise" Most equipment is marked 75 C [ August 13, 2005, 08:04 PM: Message edited by: iwire ]
Re: 60 degree ampacity Re: 60 degree ampacity Originally posted by dema: Where does it say that conductors must be sized based on the 60 degree C rating for breakers 100A and under? Click to expand... 110.14(C)(1) But it also says "unless marked otherwise" Most equipment is marked 75 C [ August 13, 2005, 08:04 PM: Message edited by: iwire ]
G GG Senior Member Location Ft.Worth, T.X. Aug 13, 2005 #3 Re: 60 degree ampacity Re: 60 degree ampacity If we were talking about NM cable (aka Romex) then 334.80 would limit you to the 60deg. ampacity rating of your conductors, but were not talking about romex so I will shut up.
Re: 60 degree ampacity Re: 60 degree ampacity If we were talking about NM cable (aka Romex) then 334.80 would limit you to the 60deg. ampacity rating of your conductors, but were not talking about romex so I will shut up.