Kohlhase

Member
If the Pump controller for this motor is service entrance rated do I need another disconnect? The CT cabinet and meter is only item between the utility pad mount and controller
 
I have a passion for unanswered threads, but I am no expert on motors. So you get what you get. :D

I offer this trembling opinion: I would say, no, you do not need another disconnect. I would then send you to Part VIII of Article 430, to peek at 430.95.

But then, I would ask, is this a motor control center or a motor controller? Because a controller is required to have a disconnecting means ahead of it by 430.102(A).

But then I'd realize, I've never seen any of this stuff in the flesh, and I quietly hit the "Post Reply" button and move on with my life.

Hey, it's a free forum. :D
 