Hooking a 60 kw generator to a manual transfer switch . 3 phase power at transfer. 120 to ground all legs. And 240 across phases.
On the load side power goes to a corner tap transformer secondary sides getting readings
A to b 240
B to c 120
A to c 120
A to ground 120
B to ground 120
C to ground 120
 
3 phase power at transfer. 120 to ground all legs. And 240 across phases.
You're reading delta and wye voltages from the same system. I don't think that's possible. :unsure:

On the load side power goes to a corner tap transformer secondary sides getting readings
A to b 240
B to c 120
A to c 120
Those voltages are even more bizarre.

A to ground 120
B to ground 120
C to ground 120
Those are normal wye voltages on a 208Y/120 system.


Are you using a voltmeter or a voltage tester?
 
None of this makes any sense. Can you post a picture of the dataplate on the transformer? Does the transformer sit between the generator and the transfer switch? If not where in the path is the transformer?
 
If the generator is ungrounded and there is no load you could get those readings as the voltage to ground would be the capacitive coupling and with a limited amount of wire and no load those readings are possible, assuming a high impedance meter was used.

Have seen the same thing with 277 volt readings to ground with a 3 phase 480 volt ungrounded system.

The voltage to ground will disappear if you use a solenoid voltage tester or a low impedance meter.
 