I peeked inside an existing panelboard, and saw green and white wires landed on the same bus. Then I noticed the feeder was only 3 phase wires and a neutral - no ground wire. I followed the feeder. It starts out as metal conduit. But then it changes to liquidtight flexible metal conduit for the last 60' of the run (that's so much easier than bending conduit and using fittings!!)
Can I have the contractor run an EGC on the outside of the LFMC and terminate it on the switchboard and the conduit?? What about 250.120(C), which requires protection for EGC's smaller than #6 (this would be a #8)? Can I have the contractor run AC cable on the outside of the LFMC?