600 amp overhead residential service what size conductors are you using

Status
Not open for further replies.

Bednarzdan

Member
Location
MA
Occupation
Master electrician
I am thinking parallel AU 350s for this 600 amp service over head is there a less expensive way, the building is a 6 family gas appliances but there is landlord 2 electric dryers in basement
There will be 7 meters and a main 600 disconnect each meter has its own main breaker feeding 7 sub panels TYIA
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Assuming you are not going to use gold..... IF your calculated load for the entire service will allow, you can use a 300kcmil, or 250kcmil CU
 