600 amp residential service change

Status
Not open for further replies.

djd

Senior Member
my dilemma is still should I upgrade this split buss 400 amp service to a 400 amp non split bus panel . He`s got about 9k sq.ft. and is adding about another 3k. and a bowling lane in future. I know I do need to do the the load calcs now , he has gas , I just have to please the inspector. Why here is I dont think they make a all in one 600 meter main breaker panel with 42 spaces . I`m looking at separate meter , disconnect and panel . Throw some info if anybodys has any . he has limited space thats my concern ,I know 400 would hold but worry about passing inspec.The service now is in a closet will all communication 8 feet wide at the most .
 

d0nut

Senior Member
Location
Omaha, NE
Depending on how the additions lay out, you could replace the existing panel in place with a similar sized panel. Then you could provide a larger service in the addition (where you can get the space you need for your equipment) and backfeed the existing distribution from your new service.
 

djd

Senior Member
Depending on how the additions lay out, you could replace the existing panel in place with a similar sized panel. Then you could provide a larger service in the addition (where you can get the space you need for your equipment) and backfeed the existing distribution from your new service.
They do not make a 600 amp all in one that I know about. Usually with a 600 amp service you need to use CT's.... I would check with the engineering dept. at the power company.
They do not make a 600 amp all in one that I know about. Usually with a 600 amp service you need to use CT's.... I would check with the engineering dept. at the power company.
You do know I`m talking residential , I can honestly say that only have one my career ,the discon
Depending on how the additions lay out, you could replace the existing panel in place with a similar sized panel. Then you could provide a larger service in the addition (where you can get the space you need for your equipment) and backfeed the existing distribution from your new service.
That would be a good idea , the utility runs about 200 + underground to the street with a junction in between he`s built a retaining wall blocking it now . This is kinda being done of a napkin , he has plans drawn , but just told me about the bowling alley , and vehicle charging stations.
nect was near the street. We are waiting to here back from the utility. They may use cts , I havent done enough residential to know .
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
One of the power company's around here allows a special 600 amp meter base but no panel for breakers. I believe they are specially made for this company. There are CT's inside the meter base. I have installed 2 or 3 of them and they cost about $1000.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
One of the power company's around here allows a special 600 amp meter base but no panel for breakers. I believe they are specially made for this company. There are CT's inside the meter base. I have installed 2 or 3 of them and they cost about $1000.
I'd love to see one. That would be cool.
I've done about 2 dozen 600 amp services, always a 36x36 CT cabinet.
 
  • Like
Reactions: djd

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I'd love to see one. That would be cool.
I've done about 2 dozen 600 amp services, always a 36x36 CT cabinet.


Here are some pics.

enhance



enhance




enhance
 
Status
Not open for further replies.