stew
Senior Member
- Location
- federal way,washington
for a 600 amp service fed with 2 each 500 mcm al conductors table 250.66 calls for a gec size of 2/0 copper. The confusing part is that 250.66(A) says that the portion of the conductor that is the sole connection to grounding electrode is not required to be larger than 6 cu. can anyone explain this a bit further to clear up my muddied mind?