could a 600a service be installed using a 600a disconnect with a riser with 500mcm? the service will have to be open CT metered but is it ok to be done this way?
 
I must be missing something !! (1)500 per phase ? What size overcurrent protection ?
 
(1) set of 500s per phase rated 380 amps on a 600 amp overcurrent device ? What Code section are your relying on ?
 
(1) set of 500s per phase rated 380 amps on a 600 amp overcurrent device ? What Code section are your relying on ?

LOL! I wasnt even paying attention to my own post. i was wondering what went wrong...Me!!

The service is 600a 240v single phase 3w, if i paralleled 350mcm does that sound better?
 
LOL! I wasnt even paying attention to my own post. i was wondering what went wrong...Me!!

The service is 600a 240v single phase 3w, if i paralleled 350mcm does that sound better?

lot better
 