J_butterfield
Member
- Location
- Spokane,wa
Looking to run 2 runs of 3x 500 xhhw 1x4/0 neutral 1x2/0 ground this will feed a 600A service 300' away with a connected load of 480amps is this sized correctly for voltage drop and is neutral sized correctly? Will be pulled underground in two 4" pvc