Other then voltage drop it is fine. How much actual load you have and how much voltage drop can be tolerated will be the determining factor.

ADD:

Does "parallel 3 x 500" mean two 500 conductors per phase or three conductors per phase? Three per phase definitely probably can compensate for any voltage drop pretty well - this just a guess, I didn't do any calculations. 300 feet at 480 volts doesn't drop voltage too rapidly in general with minimum ampacity conductors for the appliction.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If it's a service, why are you installing a neutral and an equipment ground ?
 

kwired

Electron manager
Location
NE Nebraska
If it's a service, why are you installing a neutral and an equipment ground ?

I missed that. Perhaps confusion with terminology?

J_butterfield, look in art 100 for definitions relating to "service" and those relating to "feeder" as well as "branch circuits", if you are not getting what is being said about this.
 

J_butterfield

Member
Location
Spokane,wa
Other then voltage drop it is fine. How much actual load you have and how much voltage drop can be tolerated will be the determining factor.ADD:Does "parallel 3 x 500" mean two 500 conductors per phase or three conductors per phase? Three per phase definitely probably can compensate for any voltage drop pretty well - this just a guess, I didn't do any calculations. 300 feet at 480 volts doesn't drop voltage too rapidly in general with minimum ampacity conductors for the appliction.
OK taking 600A feeders to new building 300' away from existing 1200amp service will have approximately 480 amps connected load on new 600A feed. Do I not to carry over a ground? I thought I did of coarse I will connect to uFer electrode on new building. Using 2 500's per phase
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
OK taking 600A feeders to new building 300' away from existing 1200amp service will have approximately 480 amps connected load on new 600A feed. Do I not to carry over a ground? I thought I did of coarse I will connect to uFer electrode on new building. Using 2 500's per phase

If it taps directly off the service conductors coming in, it does not need a separate EGC. You wire it like a service because it is.

If it connects anywhere downstream of your main service disconnect (with its 1200A OCPD) it will be a feeder and you need to run both neutral and EGC.

In either case you need a local ground electrode (system) at the new building.
 

J_butterfield

Member
Location
Spokane,wa
If it taps directly off the service conductors coming in, it does not need a separate EGC. You wire it like a service because it is.

If it connects anywhere downstream of your main service disconnect (with its 1200A OCPD) it will be a feeder and you need to run both neutral and EGC.

In either case you need a local ground electrode (system) at the new building.

feeds off 600A disconnect downstream of 1200amp service. thank you so 2 conduits each consisting of 3x 500 xhhw 4/0 xhhw neutral and 2/0 xhhw ground is sufficient and correctly sized?
 

tomito

Member
Location
Mexico
feeds off 600A disconnect downstream of 1200amp service. thank you so 2 conduits each consisting of 3x 500 xhhw 4/0 xhhw neutral and 2/0 xhhw ground is sufficient and correctly sized?

It is correct if you don't apply derating factors like temperature and more than three current carrying conductors in the same raceway, Vd is only 1.1% with that load.
I don't know your neutral load to calculate that feeder, 2/0 is correct for the EGC by 250.122.

Tom
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
This got me thinking...I don't have 230.40 in front of me, but I don't think that could be done compliantly could it?
I do not see why not. As long as it stays outside any building until it gets to the first OCPD and is sized for the calculated load.
You might have to use multiple breakers (up to six) at the new panel instead of a single breaker though.
 
I do not see why not. As long as it stays outside any building until it gets to the first OCPD and is sized for the calculated load.
You might have to use multiple breakers (up to six) at the new panel instead of a single breaker though.

If the second structure is served by a service drop or service lateral, but if it is served by a set of service entrance conductors, which exception to 230.40 would you use?
 

kwired

Electron manager
Location
NE Nebraska
This can be more complicated by considering we now have a "service point". What is on the utility side of the service point is not covered by NEC, even though art 100 definitions define service drop and service lateral as being on the utility side of that point.

Utility sometimes does have overhead or underground feeds that supply multiple customers, and we have no control over that and neither does NEC. I believe if you supplied two underground service conductor sets to two separate buildings from the "service point" you would be NEC compliant.
 