Is parallel 3x500 al xhhw 4/0 neutral 1/0 ground sufficient for 600A 480v service 300' away installed in 4" pvc underground
If it's a service, why are you installing a neutral and an equipment ground ?
OK taking 600A feeders to new building 300' away from existing 1200amp service will have approximately 480 amps connected load on new 600A feed. Do I not to carry over a ground? I thought I did of coarse I will connect to uFer electrode on new building. Using 2 500's per phaseOther then voltage drop it is fine. How much actual load you have and how much voltage drop can be tolerated will be the determining factor.ADDoes "parallel 3 x 500" mean two 500 conductors per phase or three conductors per phase? Three per phase definitely probably can compensate for any voltage drop pretty well - this just a guess, I didn't do any calculations. 300 feet at 480 volts doesn't drop voltage too rapidly in general with minimum ampacity conductors for the appliction.
OK taking 600A feeders to new building 300' away from existing 1200amp service will have approximately 480 amps connected load on new 600A feed. Do I not to carry over a ground? I thought I did of coarse I will connect to uFer electrode on new building. Using 2 500's per phase
If it taps directly off the service conductors coming in, it does not need a separate EGC. You wire it like a service because it is.
If it connects anywhere downstream of your main service disconnect (with its 1200A OCPD) it will be a feeder and you need to run both neutral and EGC.
In either case you need a local ground electrode (system) at the new building.
If it taps directly off the service conductors coming in, it does not need a separate EGC. You wire it like a service because it is.
feeds off 600A disconnect downstream of 1200amp service. thank you so 2 conduits each consisting of 3x 500 xhhw 4/0 xhhw neutral and 2/0 xhhw ground is sufficient and correctly sized?
I do not see why not. As long as it stays outside any building until it gets to the first OCPD and is sized for the calculated load.This got me thinking...I don't have 230.40 in front of me, but I don't think that could be done compliantly could it?
I do not see why not. As long as it stays outside any building until it gets to the first OCPD and is sized for the calculated load.
You might have to use multiple breakers (up to six) at the new panel instead of a single breaker though.