mstrlucky74
Senior Member
- Location
- NJ
The engineer is calling for (2) sets of 4#300 w/1/0 in 3" conduit. If I am thinking about this correct the 75 degree column only gives you 285 amps x 2 would only be 570. I guess he's using the 90 degree column but that's unusual, right? Thanks.