I need to fuse a 600A feeder down to 200A to serve a new ATS load. Does the disconnect need to be rated at 600A 0r 200A?
I need to fuse a 600A feeder down to 200A to serve a new ATS load. Does the disconnect need to be rated at 600A 0r 200A?
If the 600A feeder protected by a 600A fuse/breaker and that the feeder will be terminated in the disconnect, then, Yes disconnect must be 600A.
I disagree that the fused disconnect means must meet or exceed the rating of the circuit supplying it.
So what you are saying is okey to install a 20A receptacle on a 60A branch circuit.
Or what is the different that OP terminate the 600A feeder in the 100 or 200A panel board instead of a 200A fused disconnect. My point being 600A feeder is protected by 600A fuse or bkr.
I need to fuse a 600A feeder down to 200A to serve a new ATS load. Does the disconnect need to be rated at 600A 0r 200A?
Do you install 15 amp switches on 20 amp circuits?
The rules are different for switches, panelboards and receptacles.
Question:
Can 14-2 wire be used for the switch leg of a light fixture where the branch circuit is protected by a 20-amp circuit breaker?
If this is prohibited by the Code, why can 15-amp switches and receptacles be used on 20-ampere circuits?