Hello All,
I've been a long time viewer of this forum but am a new member. We are a pump contractor in California and perform electrical work for some of the ag irrigation pumps we install. I have one project that is fairly simple, but I am scratching my head after trying to double check my design.
Project Details: Our customer has an existing PG&E OH service, 400A, 480V, 3PH, 4W that currently runs two 150 HP centrifugal pumps. They have drilled a new well are asking for us to provide a quote that includes a new 400 HP vertical well pump and forgo the two 150 HP pumps AND a quote for the new 400 HP capacity to run the 150 HP x 2 at the same time (starting all three seperately, of course).
For the 400 HP only option, my FLA is 447, so simply use 447 * 1.25 = 558.75, round up to a 600A service
Where I am getting a little lost is the feeder protection and if I round down, or keep at 600A?
For the 400HP + 150 HP x 2, I use 447 *1.25 + 180 + 180 = 918, round up to a 1000 A service
Do I keep my main disconnect (feeder protection) at 1000 A as well?
I did some reading on NEC 430 in attempt to answer my own question, but wound up more confused than when I started out.
Thank you for any help and I look forward to finally being a member here
I've been a long time viewer of this forum but am a new member. We are a pump contractor in California and perform electrical work for some of the ag irrigation pumps we install. I have one project that is fairly simple, but I am scratching my head after trying to double check my design.
Project Details: Our customer has an existing PG&E OH service, 400A, 480V, 3PH, 4W that currently runs two 150 HP centrifugal pumps. They have drilled a new well are asking for us to provide a quote that includes a new 400 HP vertical well pump and forgo the two 150 HP pumps AND a quote for the new 400 HP capacity to run the 150 HP x 2 at the same time (starting all three seperately, of course).
For the 400 HP only option, my FLA is 447, so simply use 447 * 1.25 = 558.75, round up to a 600A service
Where I am getting a little lost is the feeder protection and if I round down, or keep at 600A?
For the 400HP + 150 HP x 2, I use 447 *1.25 + 180 + 180 = 918, round up to a 1000 A service
Do I keep my main disconnect (feeder protection) at 1000 A as well?
I did some reading on NEC 430 in attempt to answer my own question, but wound up more confused than when I started out.
Thank you for any help and I look forward to finally being a member here