600amp 6 meter stack

Status
Not open for further replies.

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
230.71(A) permits up to six disconnecting means for each service. If each meter has a disconnect, a main should not be required.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Do these six meters constitute all the services on the building or are there more meters/services ?
 
Status
Not open for further replies.
Top