I am working on a 4 unit strip mall. We are doing all the work in units 2,3,4
Another electrician is doing unit 1 (landlords)
The other electrician installed a new 4gang meter stack
4- 200amp disconnects Square d overhead mast service
When i went to tie in my Ser i noticed that
On Phase A he used 1-350 mcm and 1-250 mcm
On Phase B he used 1-350 mcm and 1-250 mcm
On Neutral 2- 4/0 s for ground rods he used #4
Water also #4 that runs back to units 1 panel not to the stack
And all of this was Inspected and approved This all seems wrong to me
shouldn't both be the same wire size and the water ground be 4/0?