Re: 600Amp underground grounding
The note to Table 250.122 says you may have to increase the EGC, if necessary to comply with two earlier articles. Both of those articles require a low-resistance path that will facilitate operation of the overcurrent device, in the event of a fault.
Suppose we design a facility, and give our service load calculation to the utility. Suppose that we have selected EGC sizes for the various feeders and branch circuits on the basis of Table 250.122. Suppose that we hear from the utility that they changed their initial plans, and have now chosen a service transformer that would give us a much higher "available fault current." Clearly, we need to verify our design choices for the fault current ratings of the main and other panels. But I don't see how this could have any possibility of forcing us to upsize any EGCs in the facility. If you do, could you let me know how you see it happening?