Installing a new 400A panel that is being fed from a 600A buss plug. We ran 4" conduit and pulled 600MCM. Engineer we are working for supplied panel with 400A main breaker insted of main lug. When we went to term breaker we noticed it had dual lugs and would only except up to 500MCM per hole. Engineer called square D tech support and they said breaker only needs 500MCM because you are only supposed to load it to 80% therefore 500MCM is suficient. I have never heard of this. I understand for services the exceptions but this is not the case. 500MCM is only good for 380A at 75deg witch is what their lugs are rated. Engineer didnt argue with him just said OK. Our solution was to use ILSCO terminal crimps on the ends of our wires. Has anybody ran into this problem before?