>600V Transformer Primary OCPD distance

Status
Not open for further replies.

dubk

Member
New to the forum, searched but could not find an answer. Where in the NEC can I find required distance to >600V transformer primary OCPD (5kV 600A LI switch)? Thanks.
 
Even under the new rule in the 2011 code requiring a primary side disconnect, there is no restriction on the location if the remote disconnect can be locked in the open position. There is a requirement to note the location of the remote disconnect on the transformer.
450.14 Disconnecting Means. Transformers, other than
Class 2 or Class 3 transformers, shall have a disconnecting
means located either in sight of the transformer or in
a remote location. Where located in a remote location,
the disconnecting means shall be lockable, and the location
shall be field marked on the transformer.
 
Don, thanks so much for the help.

Since the switch is located a few hundred feet away, is the conductor protected at both ends, one with the primary OCPD and the other side by the secondary breaker?
 
disconnecting means distance

disconnecting means distance

don_resqcapt19, Your explaination makes perfect sense but I do not see 450.14 in NEC 2008.
 