60A feeding 30A disconnect

Status
Not open for further replies.

karlc

New member
Hey,
Question:
Is there any reason per NEC that it would not be allowable to feed a 30A, 3Phase, fused disconnect feeding a condensing unit with a 60A breaker and #6 THWN? Reason: They changed a single 45A condensing unit to two rated at 25A that are interlocked to not run simutaneously. and I'd like to use the breaker and feed we have installed

TYIA
 
The 60 amp portion of this installation is a feeder, the 30 amp portion is a branch circuit. Your feeder still has capacity to supply additional branch circuits if you ever desire to do so.
 