If I run a feeder from a breaker 60/70 deg.C rating to supply a 60A sub-panel with a main breaker 60/70 deg.C rating and I use a 90 deg.C rated conductor such as THHN would a #6 AWG based on the 75 deg.C column have suffecient ampacity or should I run #4 AWG based on the 60 deg.C column since its less than 100A? according to Art.110-14(C)(1)(a)(2 or 3)
Less than 100A or not, is not most new equipment rated at 60/70 deg.C and is this what is ment by temperature rating of terminal or connection.
any input would be helpful. I just want to be sure I,m teaching it right I'm a new teacher and I always like to play the safe side.
Less than 100A or not, is not most new equipment rated at 60/70 deg.C and is this what is ment by temperature rating of terminal or connection.
any input would be helpful. I just want to be sure I,m teaching it right I'm a new teacher and I always like to play the safe side.