Are we allowed to run 6/3 UF (or NM) to a subpanel with a 60A main OCPD? I know there is no 55A breaker; are we allowed to go to the next largest OCPD, or do we have to go with a 50A breaker or #4 wire?
 

topgone

Senior Member
Are we allowed to run 6/3 UF (or NM) to a subpanel with a 60A main OCPD? I know there is no 55A breaker; are we allowed to go to the next largest OCPD, or do we have to go with a 50A breaker or #4 wire?

A #4 wire with a 60A OCPD is good.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If you calculate the load and its 55 amps or less you can use the #6 on a 60 amp. Otherwise its a #4
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with gus-- 240.4(B) allows us to use the next size breaker if the load doesn't exceed the value of the conductor
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
Are we allowed to run 6/3 UF (or NM) to a subpanel with a 60A main OCPD? I know there is no 55A breaker; are we allowed to go to the next largest OCPD, or do we have to go with a 50A breaker or #4 wire?
Assuming it is supplied by a feeder, not a tap, the OCPD main can be darn near anything ... 60, 100, 125, 200 ...

The feeder must be protected at its source in accordance with the code.
 

peter d

Senior Member
Location
New England
I put them on 60's all the time with #6 NM or UF cable. No issues that I'm aware of since the load is rarely even close to that in a resi setting.
 