Strahan
Senior Member
- Location
- Watsontown, PA
I want to run a 60amp feeder from existing main panel to a "sub panel". Non-continuous load size to 100%. 110.14(c)(1) points me to size according to 60c column which sizes it to a 4AWG. Now digging deeper in 110.14(c)(1) my 60amp breaker is listed as 60/75 on terminals so can I size my wire to 6AWG?
With all that I'm now at 334.80 because I want to run cable. I'm hung up here because this also points me to 60c column unless proper spacing is provided. The "sub panel" will only be about 15' away and the feeder cable will be run by itself. The more I dig the deeper in confusion I get. I think I can size it to 6AWG any thoughts?
With all that I'm now at 334.80 because I want to run cable. I'm hung up here because this also points me to 60c column unless proper spacing is provided. The "sub panel" will only be about 15' away and the feeder cable will be run by itself. The more I dig the deeper in confusion I get. I think I can size it to 6AWG any thoughts?