Interpretation Varies
Interpretation Varies
In most cases, in most jurisdictions, no. Where the generator is not in sight of the building, yes, definitely. To be safe, I would ask the inspector. The applicable section: 700.12.B.6 in the 2008 NEC. It is also in 701 and 702. The question is whether the AHJ considers the generator disconnecting means to be be readily accessible.