610 Question

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Been a while since I've been in heay industry.... My opinion is that a buss duct plug (with ropes) does not meet the requireemnt of 610.31. As I read it, the disconnect itself needs to be readily accessible and, although the buss discionnect is operable from the floor, it is not readily accessible.
Using the buss plug also seems to be somewhat awkward for the required LOTO procedure.
Comments ?
 
I agree

I agree

Been a while since I've been in heay industry.... My opinion is that a buss duct plug (with ropes) does not meet the requireemnt of 610.31. As I read it, the disconnect itself needs to be readily accessible and, although the buss discionnect is operable from the floor, it is not readily accessible.
Using the buss plug also seems to be somewhat awkward for the required LOTO procedure.
Comments ?

based on article 100...
 