Re: 620.51 opinion pole
Websparky, no, the room, shaft, pit, or anything remotely associated with these particular elevators are not sprinkled. This machine room is on the roof of a ten story hospital.
Here's the real installation.
Old elevator machine room serves five elevators with old telephone switching technology for controls.
Four of the elevators are fed from a gutter which is fed from a switch board in the basement. Gutter has no disconnect, only individual disconnects tapped from feeder inside gutter for each of four elevators.
The fifth is fed from it's own feeder from basement
Owner for what ever reason decides to modernize elevators from asthetics to controls.
Old disconnects from 60's or 70's would not be within sight of the new equipment.
To keep the inconvenience to a minimum, (one elevator down at a time) we left the old disconnects in place and came off load side to new disconnects.
Local electrical inspector has no problem with this and signs off.
Enter elevator inspector, has never seen more than one disconnect in a machine room before.
Now opens NEC and sees that 620.51 says "A single means: bla bla bla: and be designed so that no pole can be operated independantly." He interprets this to mean "ONE" disconnecting means in the machine room.
Roger