Another thread brought to mind a question I had the other day.
For a disconnecting means for vehicle chargers the Code states:
625.23 Disconnecting Means. For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position.
As I read that, there is no requirement for the disconnect to be "readily accessible" from the charger, only readily accessible somewhere on the premises. Correct ?